      Hello All,

         

      Has anyone been able to successfully measure the Max voltage of a sine wave?

         

      I am routing my analog wave through a PGA before inputting into the ADCINCVR. The Clock frequency is set to 2Mhz, the CPU is set to 12Mhz. The input wave is 3Vpp @ 3840Hz with a DC bias of 1V.

         

          while(1){
              if(ADCINCVR_1_fIsDataAvailable()){                // check flag to see if last conversion is complete
                  ADCcount[0] = ADCINCVR_1_iGetDataClearFlag();    // read sample from the ADC    
                  break;
              }
          }
          ADCcount[0] = 0;
          loopCount=0;
          while (loopCount<20){
                  PRT2DR|=IO_TEST;  //DRIVE P2[0] HIGH
                  ADCcount[loopCount]=ADCINCVR_1_iGetData();
                  loopCount++;
                  PRT2DR &= ~IO_TEST;  //DRIVE P2[0] LOW 
          }

         

       

         

      After taking the 20 samples, I am looking for the highest value in the array.

         

       

         

      The problem I am running into is that I can only recover the DC offset portion of the wave.

         

      To verify the sampling frequency is sufficent, I put an o-scope on the input wave and output of PRT2DR.  I am able to see that sample is being taken at various portions of the sine wave.

         

       

         

      Any Ideas?

         

       

         

      Vlad

        • 1. Re: Measuring Amplitude of a Sine Wave
          user_14586677

          You need this test in the second loop that accumulates the samples -

             

           

             

          if(ADCINCVR_1_fIsDataAvailable())

             

           

             

          otherwise you are reading a bunch of invalid samples.

             

           

             

          But I would suggest you post a project for forum to look at. Note you also

             

          do not need to use an array, just test if current value > last value, save new

             

          value if it is, and do this over a few samples. Then reset and do again.

             

           

             

              

             

                    

             

          "File"

             

          “Archive Project”

             

              

             

           

             

                    

             

          Use Internet Explorer or Firefox to post, Chrome does not seem to work.

             

           

             

           

             

          Regards, Dana.

          • 2. Re: Measuring Amplitude of a Sine Wave
            ki.leung

            3Vpp with 1V bias, that means some portion of the time, the input is clamped to  0V.

               

            Would suggest to change the bias so that at no time would be the signal goes below 0. Best is to have it bias in the middle of your ADC range - If you want to use this method.

               

            If the signal is a pure sine wave or a wave that you know the crest factor, you can use a diode or a perfect diode circuit and apply the rectified output that to a capacitor. This would give you the peak value of the signal and by scaling with the crest factor would give you the RMS value.

            • 3. Re: Measuring Amplitude of a Sine Wave
              ki.leung

              Another problem is the ADC used can only have a max. sample rate of around 5kSPS. Unless you have a sample and hold circuit, the reading of the ADC may not be what you expected, Most likely as if the signal be thru a low pass filter

              • 4. Re: Measuring Amplitude of a Sine Wave
                user_1377889

                Whenever possible will you please upload the complete project here, there are some settings that may affect the function of your conversion. To do so, use "Designer -> File -> Archive Project" and then attach the resulting file here (DO NOT use chrome, will not work, other browsers are OK).

                   

                 

                   

                Bob

                • 5. Re: Measuring Amplitude of a Sine Wave
                  samp

                   The ADCINCVR is an integrating ATOD convertor. It integrates the input signal before converting it to a digital value.

                     

                  Supposing you have set the resolution of the ADCINCVR to 13 bits. It would integrate the input for 16.384 milliseconds (as per your settings) and do a conversion. Within the 16.384 milliseconds you would have integrated about 63 cycles of your 3840Hz sinewave input. Hence you will get only the DC component for every measurement plus a small noise caused by a portion of a full cycle not completely covered by a measurement.

                     

                  Set the sample window of the ADCINCVR to a fraction of a full cycle of your sinewave. Then you would get better results when measuring the maximum amplitude. The smaller the fraction, the more accurate the maximum amplitude wille be. As always this is a matter of tradeoffs. If you decrease the sample window, you will have to decrease the resolution.  Even at 7-bits resolution, the ADCINCVR will integrate almost a complete cycle of your 3840 Hz input; hence you will need a faster ADC. Have you considered this?

                     

                  Please tell us the resolution at which your are operating the ADCINCVR. And take care to test for data availability in the ADCINCVR before you proceed to read a sample, as suggested by Dana.

                     

                   

                     

                  Regards,

                     

                  Sampath

                  • 6. Re: Measuring Amplitude of a Sine Wave
                    user_14586677

                    Another approach would be to use DAC and Comparator, basically feed Vx

                       

                    into one side of comparator, DAC into other side, and slew DAC values until

                       

                    comparator stops triping from one sample to the next, eg. DAC value is > Vx.

                       

                    Delay DAC to DAC sample update for a few samples of input while monitoring

                       

                    comparator output.

                       

                     

                       

                    This works if input is fixed in amplitude, otherwise algorithm would have to take

                       

                    care of AM modulation effects. Maybe delay between samples would effectively

                       

                    integrate out the variation if AM is slow changing relative to Vx fundamental frequency.

                       

                     

                       

                    Regards, Dana.

                    • 7. Re: Measuring Amplitude of a Sine Wave
                      vlad.simontov

                      Thank you all for the great ideas. I added the check to see if data is available(thank you Dana), and set the resolution to 7 bit. Sampath, your explanation makes perfect as to why I am only able to see the DC bias. I will be going over the ADCINCVR datasheet to adjust ADC. Would you suggest using a different ADC? Maybe DelSig?

                         

                       

                         

                      I have attached the project.

                         

                      Thank you

                      • 8. Re: Measuring Amplitude of a Sine Wave
                        user_1377889

                        If you stick to the ADCINC component you ought to change the "CalcTime" which you set to only 1. It should be 180clock-cycles at minimum and shall be expressed in dataclock cycles which is 1/4 of your CPU-clock. Thus it should be set to 45 to 50 be on the safe side. This will give a sample-rate of 21.3 ksps according to the datasheet.

                           

                         

                           

                        When precision is not the first goal you might use an SAR with 6 bits precision which is far more faster.

                           

                         

                           

                        Bob

                        • 9. Re: Measuring Amplitude of a Sine Wave
                          user_14586677

                          Your column clock is a little high, 3 Mhz, limit is 2.67 Mhz. The datasheet has

                             

                          conflicting info on this, it shows in other statements 8 Mhz.  I will file a CASE to

                             

                          get this clarified.

                             

                           

                             

                          I see you commented out the delay after mux switching, that should stay in place.

                             

                          There is no setlling time spec, but you could run a quick test bed to get a rough idea

                             

                          of what it needs to be.

                             

                           

                             

                          You might consider just one routine to handle average, min, max, just to save code

                             

                          and MIPS since most of these involve a 20 iterations loop, put them all in one loop.

                             

                           

                             

                          Regards, Dana.

                          • 10. Re: Measuring Amplitude of a Sine Wave
                            user_1377889

                            ...  additionally when looking into your source I realize that you are wasting a lot of your precious stack space:

                               

                            All variables declared within a function are locals and will be allocated on the stack, and since main() is a function just the rx- and txData + TXTemp + outputstring take 160 bytes off your 256-byte deep stack.

                               

                            Ways out are: declare the vars as "static" or make them globally.

                               

                             

                               

                            Bob

                            • 11. Re: Measuring Amplitude of a Sine Wave
                              user_14586677

                              Bob, I did not think you were a fan of globals -

                                 

                               

                                 

                                  

                                 

                                        http://www.cypress.com/?docID=41711

                                 

                               

                                 

                              Regards, Dana.

                              • 12. Re: Measuring Amplitude of a Sine Wave
                                user_1377889

                                No, I am not. But if I would have hidden that solution you would for sure have posted that,

                                   

                                 

                                   

                                Bob

                                • 13. Re: Measuring Amplitude of a Sine Wave
                                  user_14586677

                                  No, I would not have suggested that comment on stack. Or

                                     

                                  commented on something that was hidden from me.

                                     

                                   

                                     

                                  Regards, Dana.

                                  • 14. Re: Measuring Amplitude of a Sine Wave
                                    vlad.simontov

                                    Thank you for the respones, I will be adjusting stack usage as I get closer to the end of the project.

                                       

                                    I switched to using the SAR6 and I am able to see .1 change in amplitude. With the 3840hz signal, would I be able to optimize the clocks to see a .01 change in amplitude?