My use CY8 CKIT-001 kit Measuring temperature(The sensor is pt100).For external hardware connection:RTD_4_0 and RTD_4_1 connection PT100.then Connect the RTD_4_1 to RTD_3_0 .RTD_4_4 and RTD_4_5 connection Reference(100Ω) resistor.in the end Connect the RTD_3_4 to RTD_4_4. I don't know my way such hardware connection is correct, bother everybody to help me have a look, thank you!!!(The following is my project)
Solved! Go to Solution.
- Labels:
-
PSoC 3
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
After studying Your program it appears that your ADC is only read once and your program never reads the Cal channel or increments the current mux. I am sending you another example for you to study.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
RTD_3_0 is nowhere mentioned.
Bob
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
hello,I POSC 3 RTD module was used to measure temperature, always can't display temperature, the controller now bought a lot, but the program debugging, please help me!!!!!!!Thank you very much!
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
I'm sorry I write wrong。I connection:RTD_4_0 and RTD_4_1 connection PT100.then Connect the RTD_3_1 to RTD_4_0 .RTD_4_4 and RTD_4_5 connection Reference(100Ω) resistor.in the end Connect the RTD_3_4 to RTD_4_4.But didn't read the correct temperature.The LCD has been show -0.01,Adjust the resistance box resistance and no change。
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Thank you for your reply.My project files inside the AD sampling reference benchmark will once, but the AD value more than gathering at a time.But when debugging acquisition resistance and temperature.I saw you gave me the thermistor project, I PTC temperature sensor is a bit different, but do you have any RTD course?Thank you very much.